[SOLVED] JLink stack trace 0xA5A5A5A4
  • [SOLVED] JLink stack trace 0xA5A5A5A4
    Freescale K64F, KDS 3.2, FreeRTOS-aware debugging on Windows 8.1, JLink_Windows_V612a:
    One (and only one) of the tasks shows bad stack trace information.
    Program is running fine, plenty of stack space for this task.
    Please see image attached.
    Any idea what's going on?
    Thanks!
    Best Regards, Dave
    The post was edited 1 time, last by DaveN ().
  • Hello Dave,
    in general the IDE (KDS), or precisely its GDB client, is responsible for the stack trace.
    Did you turn on any compiler optimization?
    Arne
  • Hello Dave,
    it's unlikely, that the task itself is the cause. Any suspended task is treated in the same way, so I suspect the function call xQueueGenericReceive().
    I just gave it a try using a sample project based on FreeRTOS V9.0.0 and a FRDM-K64F board, unfortunately the stack trace is OK and the task is
    suspended from within vPortYieldFromISR() called by xQueueGenericReceive():
    1. Thread #4 536805376 (Logger [P: 2]) (Suspended : Container)
    2. vPortYieldFromISR() at port.c:907 0xffa0
    3. xQueueGenericReceive() at queue.c:1,401 0x107ee
    4. LoggerTask() at Logger.c:184 0x1850
    5. 0x0
    Which version of FreeRTOS are you using? Is it possible for you to send us your queue.c file?
    Arne
  • Hi Arne - I'm also using FreeRTOS 9.0.0 (with no changes).
    IIRC other tasks using xQueueGenericReceive show normal stack trace.
    I've attached the FreeRTOSConfig.h in case that is helpful.
    Best Regards, Dave
    PS: Is 0xA5A5A4 a known special fill sequence?
  • Hello Dave,
    so far I was not able to reproduce it.
    Is it possible for you to send us the full project?
    If not, maybe you can strip it down to the specific task.
    Arne
    PS: 0xA5 is the task stack fill byte, used for stack overflow detection (freertos.org/Stacks-and-stack-overflow-checking.html).
    This might have something to do with the value seen in the stack trace...
  • Hello Dave,
    if it is not too large, just send it to segger.com/support/technical-support/
    Arne
  • Hello Dave,
    thanks for the project. You have turned on size optimization (-Os) for the debug build.
    This is the reason for the faulty stack trace. If you turn it off and rebuild the project with no optimization (-O0), it will work as expected.